# Is it possible to use 4-wire RTD in place of a 3-wire RTD at PLC

**URL:** <https://forumautomation.com/t/is-it-possible-to-use-4-wire-rtd-in-place-of-a-3-wire-rtd-at-plc/8818>\
**Category:** Field Instrumentation\
**Created:** [November 13, 2020, 9:46am UTC](https://forumautomation.com/t/is-it-possible-to-use-4-wire-rtd-in-place-of-a-3-wire-rtd-at-plc/8818 "2020-11-13T09:46:00Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [November 13, 2020, 9:46am UTC](https://forumautomation.com/t/is-it-possible-to-use-4-wire-rtd-in-place-of-a-3-wire-rtd-at-plc/8818/1 "2020-11-13T09:46:00Z")

</div>

**Can we use 4 wire RTD(PT-100) At 3 wire RTD I/O point at PLC**

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [November 13, 2020, 9:57am UTC](https://forumautomation.com/t/is-it-possible-to-use-4-wire-rtd-in-place-of-a-3-wire-rtd-at-plc/8818/2 "2020-11-13T09:57:13Z")

</div>

Yes, we can use it, but it will not do accurate temperature compensation. Because the 4th wire is used for more than 100Mtr temperature compensation. 3wire is used for less than 100mtr

---

<div class="post-metadata">

**Author:** ![carl\_e](https://forumautomation.com/letter_avatar_proxy/v4/letter/c/94ad74/32.png) [@carl\_e](https://forumautomation.com/u/carl_e)\
**Post date:** [November 18, 2020, 12:44am UTC](https://forumautomation.com/t/is-it-possible-to-use-4-wire-rtd-in-place-of-a-3-wire-rtd-at-plc/8818/3 "2020-11-18T00:44:43Z")

</div>

Yes, a 4-wire RTD can be used with a 3-wire AI card. One of the four wires is not connected, but the accuracy is as good accuracy as the 3-wire AI card can provide.

There are VERY few true 4 wire RTD AI cards for PLCs, and those are expensive, high end cards.

One PLC RTD input card claims to be 2, 3, or 4 wire but when you read the fine print, they are 3-wire inputs, where they use a jumper to ‘fake’ the 3rd wire compensation for a 2-wire RTD, and do not use the 4th wire for a 4-wire RTD.