# In double-circuit transmission lines, what phenomenon causes a distance relay to measure incorrect apparent impedance during ground faults located at or beyond the remote substation, and why does this occur?

**URL:** <https://forumautomation.com/t/in-double-circuit-transmission-lines-what-phenomenon-causes-a-distance-relay-to-measure-incorrect-apparent-impedance-during-ground-faults-located-at-or-beyond-the-remote-substation-and-why-does-this-occur/13899>\
**Category:** Electrical\
**Tags:** interviewquestions\
**Created:** [February 19, 2026, 2:28pm UTC](https://forumautomation.com/t/in-double-circuit-transmission-lines-what-phenomenon-causes-a-distance-relay-to-measure-incorrect-apparent-impedance-during-ground-faults-located-at-or-beyond-the-remote-substation-and-why-does-this-occur/13899 "2026-02-19T14:28:08Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Rabert](https://forumautomation.com/user_avatar/forumautomation.com/rabert/32/6784_2.png) [@Rabert](https://forumautomation.com/u/Rabert)\
**Post date:** [February 19, 2026, 2:28pm UTC](https://forumautomation.com/t/in-double-circuit-transmission-lines-what-phenomenon-causes-a-distance-relay-to-measure-incorrect-apparent-impedance-during-ground-faults-located-at-or-beyond-the-remote-substation-and-why-does-this-occur/13899/1 "2026-02-19T14:28:08Z")

</div>

The phenomenon is known as Mutual Coupling due to Zero-Sequence Mutual Impedance.

In double-circuit transmission lines both circuits run in parallel on the same tower.

Because of their physical proximity mutual inductive coupling exists between the circuits especially for zero-sequence currents.

During a single line-to-ground fault zero-sequence current flows through:

• Faulted line conductor,

• Earth return path,

• Ground wire (shield wire),

• Adjacent parallel circuit (healthy circuit).

This creates mutual zero-sequence voltage in the healthy (or) protected line.

## How it affects Distance Relay Measurement?

Distance relays calculate impedance using:

**Z=V/I**

However due to mutual coupling:

The relay measures additional induced voltage.

This voltage is not caused by the actual fault in the protected line.

As a result the relay calculates incorrect apparent impedance.

 ![image](https://cdn.forumautomation.com/original/2X/4/44935494becebb3aefb3670d7a8cde82c7adc602.jpeg)

## Effects on Relay Operation

| **Condition** | **Effect on Relay** |
| --- | --- |
| Mutual coupling present | Apparent impedance becomes higher or lower than actual |
| Ground fault beyond remote substation | Relay may underreach or overreach |
| Strong mutual coupling | Increased measurement error |

## Possible Relay Errors

## 1). Overreach Errors

Relay sees fault closer than actual location.

May trip incorrectly.

## 2). Underreach Errors

Relay sees fault farther than actual location.

May fail to trip when required.

## Why this occurs only for Ground Faults?

Mutual coupling mainly affects:

• Zero-sequence current,

• Ground fault protection.

It does not significantly affect:

• Phase-to-phase faults

because zero-sequence current is absent in phase faults.

## Example

Consider:

2 parallel 220 kV **[transmission lines](https://forumelectrical.com/how-to-protect-transmission-lines/)**.

Ground fault occurs beyond remote substation.

Due to mutual coupling:

Relay calculates wrong impedance.

Zone-2 protection may overreach into adjacent line.

## Mitigation Methods

• Mutual compensation factor (Km) setting in relay

• Use of numerical distance relays with mutual compensation

• Pilot protection schemes (**[Differential protection](https://forumelectrical.com/differential-protection/)**, PLCC)

> ### You can also follow us on [[color=#ff7700] **AutomationForum.co** [/color]](https://automationforum.co/), [url= [https://www.facebook.com/instrumentation.control](https://www.facebook.com/instrumentation.control)][color=#1E00A3] **Facebook** [/color][/url] and [url= [https://www.linkedin.com/showcase/81532759/feed/posts/](https://www.linkedin.com/showcase/81532759/feed/posts/)][color=#1E00A3] **Linkedin** [/color][/url] to receive daily Instrumentation updates.

> ### You can also follow us on [[color=#ff7700] **ForumElectrical.com** [/color]](https://forumelectrical.com/), [[color=#1E00A3] **Facebook** [/color]](https://www.facebook.com/profile.php?id=100091841583670) and [[color=#1E00A3] **Linkedin** [/color]](https://www.linkedin.com/showcase/91130242/feed/posts/) to receive daily Electrical updates.