# If the vessel filled with heavier density fluid so an interface level transmitter should show

**URL:** <https://forumautomation.com/t/if-the-vessel-filled-with-heavier-density-fluid-so-an-interface-level-transmitter-should-show/9175>\
**Category:** Field Instrumentation\
**Created:** [February 17, 2021, 4:57am UTC](https://forumautomation.com/t/if-the-vessel-filled-with-heavier-density-fluid-so-an-interface-level-transmitter-should-show/9175 "2021-02-17T04:57:15Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [February 17, 2021, 4:57am UTC](https://forumautomation.com/t/if-the-vessel-filled-with-heavier-density-fluid-so-an-interface-level-transmitter-should-show/9175/1 "2021-02-17T04:57:16Z")

</div>

Interface level transmitter output is

A: Zero

B : 50%

C : 100%

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [February 17, 2021, 5:07am UTC](https://forumautomation.com/t/if-the-vessel-filled-with-heavier-density-fluid-so-an-interface-level-transmitter-should-show/9175/2 "2021-02-17T05:07:48Z")

</div>

Interface level transmitter output is

LRV = 4 mA when tank is fully filled with lighter fluid

URV = 20 mA when tank is fully filled with heavier fluid

4mA (0%) when tank is fully filled with lighter fluid and 20mA (100%) when tank is fully filled with heavier fluid and at 50% interface means 50% heavier fluid and 50% lighter fluid