> # How to Set the Load Settings on an ACB?

Air Circuit Breaker (ACB) is an essential component in electrical systems that protects the circuit from

- Overload and
- Short Circuit.

The ACB configuration must be done appropriately to ensure the system’s safety and efficiency.

 ![image](https://cdn.forumautomation.com/original/2X/1/1d241df892fbbedf64670be3650b518d1f1f782a.jpeg)

Today, we’ll talk about how to set 80% load & what parameters should be considered.

> # Ir (Overload Protection Settings)

 

Ir stands for Overload Protection, and it is set as a percentage of load current.

 

For an 80% load, IR = 0.8ln (In - nominal current).

 

**Ex:** If the nominal current (In) is 1000A, then Ir = 0.8 x 1000 = 800A

 

> # TR (Time Delay For Overload Protection)

 

TR is the time after that the breaker will trip due to overload.

 

It is often expressed in seconds & adjusted based on the type of load.

 

If tr = 10s is selected, the breaker will trip if 800A current flows for more than 10 seconds.

 

> # ISD (Short Circuit Protection Settings)

 

ISD stands for Short Circuit Protection, and it is activated when a short circuit current is present.

 

It is typically configured as a multiple of IR, such as 5xlr (or) 10xlr.

 

**Ex:** If IR = 800A then ISD = 5 x 800 = 4000A.