## **How to select the Right Inverter Rating?**

## 1. Calculate the Total Connected Load

 ![image](https://cdn.forumautomation.com/original/2X/5/5359a21501ee37957ecfc0bdab0d7e5dbffc7493.png)

## 2. Apply a Safety Margin

Total Load = 370 × 1.25 = 462.5 W

## 3. Calculate the Inverter VA Rating

Assuming an inverter power factor of 0.8:

**[Inverter Rating](https://forumelectrical.com/ups-inverter-battery-backup-time-calculation-with-load-calculation-and-battery-selection-charts/)** = 462.5 / 0.8 = 578.1 VA

Recommended Selection: 600 VA minimum based on the calculated load. Consider a higher-rated inverter after checking motor starting surge, battery voltage and manufacturer specifications.