# How to select the correct Potential Transformer rating for Protection and Metering?

**URL:** <https://forumautomation.com/t/how-to-select-the-correct-potential-transformer-rating-for-protection-and-metering/13839>\
**Category:** Electrical\
**Tags:** interviewquestions\
**Created:** [January 21, 2026, 5:58am UTC](https://forumautomation.com/t/how-to-select-the-correct-potential-transformer-rating-for-protection-and-metering/13839 "2026-01-21T05:58:02Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Rabert](https://forumautomation.com/user_avatar/forumautomation.com/rabert/32/6784_2.png) [@Rabert](https://forumautomation.com/u/Rabert)\
**Post date:** [January 21, 2026, 5:58am UTC](https://forumautomation.com/t/how-to-select-the-correct-potential-transformer-rating-for-protection-and-metering/13839/1 "2026-01-21T05:58:02Z")

</div>

A [url= [Potential Transformer (PT) Testing Procedure](https://forumelectrical.com/potential-transformer-pt-testing-procedure/)][color=#1E00A3] **Potential Transformer (PT)** [/color][/url] steps down high system voltage to a safe, standardized low voltage for:

 ![image](https://cdn.forumautomation.com/original/2X/0/07a4523361ab6aae40e15be7fcda95a89b80de64.jpeg)

1). Metering (energy, voltage, power)

2). Protection relays

3). Control and indication circuits

It must:

• Maintain voltage accuracy

• Withstand system overvoltages

• Supply required VA burden without excessive error

## PT Primary Voltage Selection

### a) Based on System Voltage

Potential Transformer (PT) primary rating must match system [url= [Line To Phase Voltage Calculator](https://forumelectrical.com/line-to-phase-voltage-calculator/)][color=#1E00A3] **phase voltage.** [/color][/url]

Voltage. PT Primary (Star)

11 KV 11 / √3 = 6.35kV

33 KV 33 / √3 = 19.05kV

66 kV 66 / √3 = 38.1kV

132 kV 132 / √3 = 76.2kV

Star-connected PTs are most common in most of substations.

## PT Secondary Voltage Selection

Standard secondary voltages:

1). 110 V (most common)

2). 110 / √3 = 63.5 V (phase voltage)

3). 100 V (some standards)

Modern relays are designed for 110 V seconds.

## PT Burden Calculation (IMP)

Burden is the total VA load connected to the Potential Transformer (PT) secondary.

It includes:

1). Protection relays

2). Metering devices

3). Indicating instruments

4). Cable losses

Device: Burden (VA)

Numerical protection [url= [Phase Failure Relay (Voltage Monitoring Relay): Complete Guide for Three-Phase Motor Protection](https://forumelectrical.com/phase-failure-relay-voltage-monitoring-relay-complete-guide-for-three-phase-motor-protection/)][color=#1E00A3] **relay:** [/color][/url] 10VA

Energy meter: 5 VA

Voltmeter: 2 VA

Selector switch + wiring: 3 VA

Total Actual Burden = 10 + 5 + 2 + 3 = 20 VA

## Apply Engineering Margin

PT should never be operated at full rated burden.

Recommended margin:

20–30%

Required VA = 20 x 1.25 = 25VA

## Selection of PT VA Rating

PTs are manufactured in standard VA ratings:

25 VA

50 VA

100 VA

200 VA

Always select the next higher standard rating.

Selected PT Rating = 50 VA

## Accuracy Class Selection

Accuracy class defines maximum permissible voltage error.

**Metering PT**

Used for billing & measurement:

- Class 0.2
- Class 0.5

Lower number = higher accuracy.

Protection PT

Used for relays:

- Class 3P
- Class 6P

Protection PT focuses primarily on voltage fidelity during faults not billing accuracy.

## Voltage Factor (Overvoltage Capability)

PT must withstand temporary overvoltages during:

- Earth faults
- Switching
- Ferroresonance

System Earthing. Voltage Factor

Solidly earthed. 1.2 continuous

Isolated / unearthed. 1.9 for 8 hours

Always check utility / grid code requirement.

## Insulation Level

PT insulation must match system BIL.

**Example for 11 kV PT:**

Rated insulation: 12/28/75 kV

- 12 kV → highest system voltage
- 28 kV → power frequency withstand
- 75 kV → lightning impulse

## PT Connection Types

Star–Star → Metering + protection

Open Delta (V-V) → Residual voltage (earth fault detection)

Broken Delta → Zero-sequence voltage (3V₀)

## Typical PT Sizing

**Example**

System: 11 kV, solidly earthed

Secondary: 110 V

Total burden: 20 VA

Margin: 25%

Calculation:

20 x 1.25 = 25 VA

Final Selection:

- PT Ratio: 11 kV / 110 V
- VA Rating: 50 VA
- Accuracy: 0.5 (metering) + 3P (protection)
- Voltage Factor: 1.2 continuous.

> ### You can also follow us on [[color=#ff7700] **AutomationForum.co** [/color]](https://automationforum.co/), [url= [https://www.facebook.com/instrumentation.control](https://www.facebook.com/instrumentation.control)][color=#1E00A3] **Facebook** [/color][/url] and [url= [https://www.linkedin.com/showcase/81532759/feed/posts/](https://www.linkedin.com/showcase/81532759/feed/posts/)][color=#1E00A3] **Linkedin** [/color][/url] to receive daily Instrumentation updates.

> ### You can also follow us on [[color=#ff7700] **ForumElectrical.com** [/color]](https://forumelectrical.com/), [[color=#1E00A3] **Facebook** [/color]](https://www.facebook.com/profile.php?id=100091841583670) and [[color=#1E00A3] **Linkedin** [/color]](https://www.linkedin.com/showcase/91130242/feed/posts/) to receive daily Electrical updates.