# How to measure loop current using Test diode?

**URL:** <https://forumautomation.com/t/how-to-measure-loop-current-using-test-diode/3005>\
**Category:** Calibration\
**Created:** [January 19, 2018, 9:07pm UTC](https://forumautomation.com/t/how-to-measure-loop-current-using-test-diode/3005 "2018-01-19T21:07:32Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![sivaranjith](https://forumautomation.com/letter_avatar_proxy/v4/letter/s/ba9def/32.png) [@sivaranjith](https://forumautomation.com/u/sivaranjith)\
**Post date:** [January 19, 2018, 9:07pm UTC](https://forumautomation.com/t/how-to-measure-loop-current-using-test-diode/3005/1 "2018-01-19T21:07:33Z")

</div>

Measuring the loop current using test diode is one of the important troubleshooting methods. A Test diode can be placed anywhere in the current loop forward biased.

 ![](https://cdn.forumautomation.com/original/2X/5/575a319336c83aec44a99a8cb99059f00332cc09.png)

The rectifying diode can be placed in series at anywhere in the loop.

- During normal condition the diode conducts easily, that only shows a drop of 0.7 V which is common for forward biased silicon diode.

- To measure the loop current, we connect an ammeter parallel to a diode.

 ![](https://cdn.forumautomation.com/original/2X/3/3c2651f15a1753410795b5040cd767c2a692ef46.png)

- The ammeter resistance is much lower than the diode resistance.

- As current tends to flow through lower resistance path, the loop current flow through the ammeter.

- Without enough current to bais the diode, entire current flows through the ammeter. the diode effectively turns off and conducts 0 mA, leaving the entire loop current to pass through the ammeter.

- During this current flow the ammeter reads the amount of current through the loop.

- When the ammeter is disconnected the diode resistance produce a 0.7V again and starts to conduct again.

- Such a diode may be installed at the nearest junction box, between terminals on a terminal strip, or even incorporated into the transmitter itself. Some process transmitters have an extra pair of terminals labelled “Test” for this exact purpose.

 ![](https://cdn.forumautomation.com/original/2X/c/c4cb0b6dd8eb483acbb4d4e95b6a3ecdce26e769.png)

- Ammeter is connected to the terminals labelled as “TEST” below and to the right of the main screw terminals where the loop wiring attaches.

- Transmitters equipped with analog meter movements for direct visual indication of the 4-20 mA signal usually connect the analog milliammeter in parallel with just such a diode.

---

<div class="post-metadata">

**Author:** ![7orrass](https://forumautomation.com/letter_avatar_proxy/v4/letter/7/6f9a4e/32.png) [@7orrass](https://forumautomation.com/u/7orrass)\
**Post date:** [January 23, 2018, 7:16am UTC](https://forumautomation.com/t/how-to-measure-loop-current-using-test-diode/3005/2 "2018-01-23T07:16:29Z")

</div>

This does not work for 0 to 20 mA ? because near 0 mA the current is too low to pass through the diode ! Thank you