# How to do the configuration of DP type flow meter in FF

**URL:** <https://forumautomation.com/t/how-to-do-the-configuration-of-dp-type-flow-meter-in-ff/9192>\
**Category:** Field Instrumentation\
**Created:** [February 22, 2021, 8:19am UTC](https://forumautomation.com/t/how-to-do-the-configuration-of-dp-type-flow-meter-in-ff/9192 "2021-02-22T08:19:11Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [February 22, 2021, 8:19am UTC](https://forumautomation.com/t/how-to-do-the-configuration-of-dp-type-flow-meter-in-ff/9192/1 "2021-02-22T08:19:12Z")

</div>

Explain how to configure the DP flow meter in FF

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [February 22, 2021, 8:24am UTC](https://forumautomation.com/t/how-to-do-the-configuration-of-dp-type-flow-meter-in-ff/9192/2 "2021-02-22T08:24:40Z")

</div>

check the transmitter range and DCS range, square root, first you see calibration datasheet, square & Linear type, then you set up and connect Hart and check the tag number, range input-output, after apply value transmitter range showing transmitter display and DCS output range square root, apply 25%, output showing 50.5%, you give 50% and DCS could show 70.7%, you give 75%, display and DCS could show 86.6%, you give 100%, display and DCS could show 100%.

---

<div class="post-metadata">

**Author:** ![carl\_e](https://forumautomation.com/letter_avatar_proxy/v4/letter/c/94ad74/32.png) [@carl\_e](https://forumautomation.com/u/carl_e)\
**Post date:** [March 25, 2021, 2:29pm UTC](https://forumautomation.com/t/how-to-do-the-configuration-of-dp-type-flow-meter-in-ff/9192/3 "2021-03-25T14:29:18Z")

</div>

For Foundation Fieldbus (FF), the Analog input block in the transducer group has the settings for pressure and flow.

L\_Type is set to “Indirect” if the transmitter implements the square root function; Direct if the output is pressure, not flow.

XD\_SCALE is the pressure range corresponding to 0-100% flow rate, according to the primary flow element sizing sheet. XD\_SCALE is in units of percent.

OUT\_SCALE is flow rate units and scaling LOW\_CUT is low flow cut-off

OUT is the scaled flow output.