# How to calculate the output of the pressure transmitter

**URL:** <https://forumautomation.com/t/how-to-calculate-the-output-of-the-pressure-transmitter/8766>\
**Category:** Field Instrumentation\
**Created:** [October 31, 2020, 3:21pm UTC](https://forumautomation.com/t/how-to-calculate-the-output-of-the-pressure-transmitter/8766 "2020-10-31T15:21:39Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [October 31, 2020, 3:21pm UTC](https://forumautomation.com/t/how-to-calculate-the-output-of-the-pressure-transmitter/8766/1 "2020-10-31T15:21:40Z")

</div>

**A pressure transmitter has a calibrated measurement range of 200 to 300 PSIG, and an output range of 4-20 mA. What is the expected output if the input pressure is 235 PSIG?**

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [October 31, 2020, 3:22pm UTC](https://forumautomation.com/t/how-to-calculate-the-output-of-the-pressure-transmitter/8766/2 "2020-10-31T15:22:40Z")

</div>

00 to 300 PSIG=100 PSIG

```
 35/100=0.35 PSIG

 0.35 to mA x16+4=9.6mA

```