Describe the calculation of LRV and URV of dp transmitter in open tank… Tank Height 17400 mm Specific gravity 1.89

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [April 8, 2021, 12:41pm UTC](https://forumautomation.com/t/how-to-calculate-lrv-urv-dp-transmitter-in-an-open-tank/9310/2 "2021-04-08T12:41:08Z")

</div>

Range=Height × S. G

=17400× 1.89

=32886mmwc

So., calibration range LRV is 0 mmwc and URV is 32886 mmwc