# How much upstream and downstream straight length run is needed for an orifice plate flow measurement?

**URL:** <https://forumautomation.com/t/how-much-upstream-and-downstream-straight-length-run-is-needed-for-an-orifice-plate-flow-measurement/9089>\
**Category:** Field Instrumentation\
**Created:** [January 22, 2021, 12:31pm UTC](https://forumautomation.com/t/how-much-upstream-and-downstream-straight-length-run-is-needed-for-an-orifice-plate-flow-measurement/9089 "2021-01-22T12:31:16Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [January 22, 2021, 12:31pm UTC](https://forumautomation.com/t/how-much-upstream-and-downstream-straight-length-run-is-needed-for-an-orifice-plate-flow-measurement/9089/1 "2021-01-22T12:31:16Z")

</div>

What is the required upstream and downstream straight length run that is suitable for an orifice plate flow measurement

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [January 22, 2021, 12:45pm UTC](https://forumautomation.com/t/how-much-upstream-and-downstream-straight-length-run-is-needed-for-an-orifice-plate-flow-measurement/9089/2 "2021-01-22T12:45:13Z")

</div>

5D-10D minimum for straight horizontal pipe length will be increased depends upon the number of bends in the pipe. 10D to 15 D at the Inlet and 5D to 7D at the outlet

---

<div class="post-metadata">

**Author:** ![carl\_e](https://forumautomation.com/letter_avatar_proxy/v4/letter/c/94ad74/32.png) [@carl\_e](https://forumautomation.com/u/carl_e)\
**Post date:** [January 28, 2021, 9:03pm UTC](https://forumautomation.com/t/how-much-upstream-and-downstream-straight-length-run-is-needed-for-an-orifice-plate-flow-measurement/9089/3 "2021-01-28T21:03:20Z")

</div>

The upstream/downstream straight run requirements can be quite significant for flow obstructions without the use of flow straightening conditioners - in one case as high as 75 upstream diameters.

Both ISO 5167-2 (Orifice Plates) 2012 and ASME-MFC-3M (2004) standards have similar, if not identical charts with experimentally determined requirements, but there’s an entire page of listing additional considerations.

 ![Minimum upstream downstream diameters IEC-5167-2, 2003](https://cdn.forumautomation.com/original/2X/e/e88f09b8a8d94b48e79a83d04d7b051ae5542a33.png) [Straight run upstream-downstream for Orifice plate requirements, ISO 5167-2, 2003.pdf](https://forumautomation.com/uploads/short-url/hy0ZVjLUmKDBhBVuOHRjz4Lgzkm.pdf) (96.4 KB)