\*\*In a control valve its opening time is 4 seconds and closing time is 8 seconds and how can we make both the opening and closing in 4 seconds \*\*

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [December 28, 2020, 5:48am UTC](https://forumautomation.com/t/how-can-we-control-the-opening-time-and-closing-time-in-a-control-valve/9014/2 "2020-12-28T05:48:23Z")

</div>

Check at what mA does it start moving

Check the exhaust

Increase positioned gain

Perform bench settings