# How can we check the control valve passing?

**URL:** <https://forumautomation.com/t/how-can-we-check-the-control-valve-passing/9088>\
**Category:** Field Instrumentation\
**Created:** [January 21, 2021, 8:01am UTC](https://forumautomation.com/t/how-can-we-check-the-control-valve-passing/9088 "2021-01-21T08:01:22Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [January 21, 2021, 8:01am UTC](https://forumautomation.com/t/how-can-we-check-the-control-valve-passing/9088/1 "2021-01-21T08:01:23Z")

</div>

**What are the steps to check the control valve passing**

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [January 21, 2021, 8:21am UTC](https://forumautomation.com/t/how-can-we-check-the-control-valve-passing/9088/2 "2021-01-21T08:21:04Z")

</div>

Make the valve fully shut, and keep one pressure gauge on the downstream side drain point. If the pressure gauge shows any value then you can make sure there is passing. Close upstream and downstream manual valve. Close Control Valve. Slowly open the downstream valve and listen for flow. Try a few times. If you hear flow, your control valve is leaking by.