# Honeywell DCS controller- High Performance Manager(HPM) IOP- LLMUX card shows ISF error and in diagnostic it shows FTA missing

**URL:** <https://forumautomation.com/t/honeywell-dcs-controller-high-performance-manager-hpm-iop-llmux-card-shows-isf-error-and-in-diagnostic-it-shows-fta-missing/401>\
**Category:** Honeywell\
**Created:** [April 18, 2015, 6:04pm UTC](https://forumautomation.com/t/honeywell-dcs-controller-high-performance-manager-hpm-iop-llmux-card-shows-isf-error-and-in-diagnostic-it-shows-fta-missing/401 "2015-04-18T18:04:57Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumen](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/65b543/32.png) [@instrumen](https://forumautomation.com/u/instrumen)\
**Post date:** [April 18, 2015, 6:04pm UTC](https://forumautomation.com/t/honeywell-dcs-controller-high-performance-manager-hpm-iop-llmux-card-shows-isf-error-and-in-diagnostic-it-shows-fta-missing/401/1 "2015-04-18T18:04:59Z")

</div>

Solution:-

1. Connect the FTA cable properly and reset the card.
2. Load database in card. ( restore module)
3. Make it in run state.