# General calibration procedure for differential pressure transmitters

**URL:** <https://forumautomation.com/t/general-calibration-procedure-for-differential-pressure-transmitters/2942>\
**Category:** Calibration\
**Tags:** pressure\
**Created:** [January 9, 2018, 8:49pm UTC](https://forumautomation.com/t/general-calibration-procedure-for-differential-pressure-transmitters/2942 "2018-01-09T20:49:28Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![sivaranjith](https://forumautomation.com/letter_avatar_proxy/v4/letter/s/ba9def/32.png) [@sivaranjith](https://forumautomation.com/u/sivaranjith)\
**Post date:** [January 9, 2018, 8:49pm UTC](https://forumautomation.com/t/general-calibration-procedure-for-differential-pressure-transmitters/2942/1 "2018-01-09T20:49:30Z")

</div>

Calibrating a [differential pressure transmitter](https://forumautomation.com/t/basic-working-of-differential-pressure-transmitter/2611) is much more difficult than calibrating a pressure transmitter. This is because the pressures are very small. So low-pressure gauges are used to calibrate the differential pressure gauge.

In industries, calibration is done using devices like [Wallace & Tiernan](https://forumautomation.com/t/wallace-tiernan-pneumatic-calibrator/2465) calibrator. Understand the port connections of the Wallace & Tiernan calibrator.

![](https://cdn.forumautomation.com/original/2X/2/21a193ae2ef0eec5a207ded05256206f82b3e5e9.png)

> ##calibration steps for pneumatic differential pressure transmitter:

- Connect the calibrated pressure supply to the HIGH inlet pressure. Leave the LOW pressure inlet connection open.

- Connect the air supply port to the 20 psi (1.4 bar) supply.

- Use a pressure gauge to cover the range 0 - 20 psi (0 - 1.4bar). Connect it to the output port.

- Using the manufacturer’s manual set up the differential pressure transmitter to values given by the instructor.

- Use the results to draw a calibration curve in the same way as for a pressure gauge. Ensure the device gives a linear output of 3-15 psi (0.2-1 bar). Check its accuracy is within specification. Remember: 3-15 psi is not equivalent to 0.2-1bar. Calibrate using either 3-15 psi or 0.2-1 bar.

> ##calibration steps for electrical differential pressure transmitter:

- Connect the “HIGH” inlet pressure connection to the calibrated pressure supply. Leave the “LOW” pressure connection open.

- Connect up the 24V D.C. supply to the transmitter output terminals using the manufacturer’s calibration manual.

- The calibration method depends on the manufacturer. You may or may not need a series load resistor. The device may be current or voltage calibrated. The manual must be used.

- Set up the differential pressure transmitter to values given by the instructor.

- From results obtained in the same way as for a pressure gauge, draw a calibration curve. Ensure the device gives a linear output (4 - 20 mA) and check its accuracy is within specification.