HMI always shows this message what will be the reason for this fault. It is not the problem of the communication cable I already change that, please give a solution for this problem

![image](https://cdn.forumautomation.com/original/2X/6/6c0b95994a15e72e193fa85715914ff52457a90d.jpeg)

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [June 16, 2021, 4:30am UTC](https://forumautomation.com/t/faults-in-hmi-plc-response-problems/9508/2 "2021-06-16T04:30:48Z")

</div>

- Use a twisted pair cable, this problem could be because of harmonics, and check earthing in the panel can be also helpful.

- Change the parity bit and then upload

- Check any VFD or electronic device harmonic is preset

- Check communication parameters

- Check if you have external 24 VDC in the plc

- Check the IP’s of both HMI and the PLC