Dry Type Transformer Nameplate based on IEC 60076

## (1). Manufacturer

This indicates the company that manufactured the **[transformer.](https://forumelectrical.com/oil-leak-test-for-power-transformers-step-by-step-testing-procedure/)**

## (2). Type: SWD 2000/13.8

This is the model number of the transformer.

2000 represents the rated capacity in **[kVA.](https://forumelectrical.com/kva-kw-ampere-amp-chart/)**

13.8 represents the high voltage (HV) rating in kV.

## (3). Serial Number (S/N): 054092301

A unique identification number assigned to the transformer.

## (4). Rated Power: 2000 kVA

The transformer can handle a maximum load of 2000 kVA.

## (5). Winding Material: Al/Al

Both **[High Voltage (HV)](https://forumelectrical.com/high-voltage-hv-motor-megger-test-procedure/)** and **[Low Voltage (LV)](https://forumelectrical.com/low-voltage-cubicle-switchboard-lvsb-assessment-and-testing-protocol/)** windings are made of aluminum.

## (6). Rated Voltage (HV Tap Positions)

POS-1: 14490 V

POS-2: 14145 V

POS-3: 13800 V (Nominal)

POS-4: 13455 V

POS-5: 13110 V

These are tap changer positions used to adjust voltage without load (Off-Circuit Tap Changer).

## (7). Standard: IEC 60076-11

International standard for dry-type transformers.

## (8). Manufacturing Year: 2024

The year in which the transformer was manufactured.

 ![2](https://cdn.forumautomation.com/original/2X/9/922f921fb5527075951c30b93086d4f6ad428262.jpeg)

## (9). Frequency: 60 Hz

Designed for operation in a 60 Hz power system (commonly used in Middle East regions).

## (10). Vector Group: Dyn11

Indicates winding configuration:

Primary (HV): Delta connection

Secondary (LV): Star connection with neutral

Phase shift: +30°

## (11). Type of Cooling: AN (Air Natural)

Cooling is achieved naturally using air without any forced cooling system.

## (12). Protection of Transformer: IP00

No enclosure protection; internal parts are exposed (open type).

## (13). Protection of Enclosure: IP31

The enclosure provides:

Protection against objects larger than 4 mm

Protection against vertical water droplets

## (14). Weight: 5300 kg

Total weight including enclosure.

## (15). Rated Current

HV Side: 83.67 A (Primary)

LV Side: 2886.8 A (Secondary)

(16) Um: 17.5 kV

Maximum system voltage on the HV side.

## (17). Insulation Level

HV: LI 95 kV / AC 38 kV

LV: AC 5 kV

Indicates lightning impulse and power frequency withstand capability.

## (18). Short Circuit Impedance (at 75°C): 4.35%

Limits short circuit current and provides internal impedance.

## (19). Maximum Short Circuit Duration: 3 Seconds

The transformer can withstand short circuit conditions for up to 3 seconds.

## (20). Maximum Ambient Temperature: 50°C

Maximum allowable surrounding temperature during operation.

## (21). Temperature Rise: 150°C

Maximum temperature rise of the winding under full load.

## (22). Insulation Class: F/F

Class F insulation with a maximum temperature limit of 155°C.

## (23). Environmental Class: E2

Suitable for industrial environments with moderate pollution.

## (24). Climatic Class: C2

Can operate in low temperature conditions.

## (25). Fire Behavior Class: F1

Low smoke emission and reduced fire spread, making it safer for buildings.

## (26). Type of Service: Continuous

Designed for 24/7 continuous operation.

## (27). Enclosure Color: RAL 7032

Standard color code of the transformer body.

## (28). Connection Diagram

HV Side: U1 – V1 – W1

LV Side: u2 – v2 – w2

## (29). Off-Circuit Tap Changer

**[Tap positions](https://forumelectrical.com/transformer-tap-changing-working-principle/)** (POS 1 to POS 5) are used to increase or decrease voltage, but adjustment must be done when the transformer is de-energized (no load condition).

## Summary

This nameplate provides complete technical details of the **[transformer](https://forumelectrical.com/power-transformer-pre-commissioning-checklist/)**, including rating, voltage levels, insulation, protection, cooling method, and operating conditions, which are essential for proper installation, operation, and maintenance.