# Does a Metallic Cable Tray Require Earthing or Bonding?

**URL:** <https://forumautomation.com/t/does-a-metallic-cable-tray-require-earthing-or-bonding/12906>\
**Category:** Electrical\
**Tags:** interviewquestions\
**Created:** [December 18, 2024, 5:11am UTC](https://forumautomation.com/t/does-a-metallic-cable-tray-require-earthing-or-bonding/12906 "2024-12-18T05:11:54Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Instrument\_Engineer](https://forumautomation.com/user_avatar/forumautomation.com/instrument_engineer/32/6734_2.png) [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Post date:** [December 18, 2024, 5:11am UTC](https://forumautomation.com/t/does-a-metallic-cable-tray-require-earthing-or-bonding/12906/1 "2024-12-18T05:11:54Z")

</div>

## Does a Metallic Cable Tray Require Earthing or Bonding?

 ![image](https://cdn.forumautomation.com/original/2X/8/80fea6b72304d88a27b6fd896dc90d5043858a61.jpeg)

The necessity of earthing or bonding a metallic cable tray depends on its role in the electrical system. The tray may require earthing, bonding, or neither, depending on whether it qualifies as an exposed-conductive-part or an extraneous-conductive-part.

### Exposed-Conductive-Part:

A conductive part of equipment that can be touched, is not normally live, but could become live under fault conditions.

Purpose of earthing: To provide a fault current path for operating the overcurrent protective device.

### Extraneous-Conductive-Part:

A conductive part that can introduce a potential (e.g., Earth potential) into the system but is not part of the electrical installation.

Purpose of bonding: To prevent potential differences and reduce shock risks.

## Evaluating the Need for Earthing

### Is the metallic tray an exposed-conductive-part?

### Tray Used as a Protective Conductor

If the tray itself is used to carry fault currents (per Regulation 543.2.1), it is an exposed-conductive-part and must be earthed.

### Tray Not Used as a Protective Conductor

Scenario 1: The tray carries metallic-sheathed cables (e.g., MICC cables).

The cable sheath provides the fault current path, so the tray is not an exposed-conductive-part and does not require earthing.

Note: Earthing the tray could distribute touch voltages unnecessarily during a fault.

Scenario 2: The tray carries cables with non-metallic sheaths.

These cables provide equivalent protection to Class II equipment, ensuring no fault current flows through the tray.

The tray is not an exposed-conductive-part and does not require earthing.

Caution: Earthing in this case may increase shock risks.

## Evaluating the Need for Bonding

### Is the metallic tray an extraneous-conductive-part?

### Potential Introduction of Earth Potential

- If the tray introduces Earth potential from outside the installation (e.g., carrying cables into a building and contacting Earth externally), it qualifies as an extraneous-conductive-part.
- In this case, bonding is required to mitigate potential differences.

### No Introduction of External Potential

- If the tray does not introduce a new potential, it is not an extraneous-conductive-part and does not require bonding.

## Special Considerations

### Metallic Conduit or Trunking

- Houses insulated cables without an outer sheath and inherently provides a fault path. Earthing may be required depending on its use.

### Cable Basket

- Similar principles apply as for metallic trays, depending on its role in fault current paths or potential introduction.

Earthing is required if the tray is an exposed-conductive-part and used as a protective conductor.

Bonding is required if the tray is an extraneous-conductive-part that introduces an Earth potential.

Neither is needed if the tray is neither an exposed-conductive-part nor an extraneous-conductive-part.

Always refer to local electrical regulations (e.g., IEC, BS 7671) for specific requirements.