# Difference between Calibration & Ranging, What is Up-tests and Down-tests in calibration?

**URL:** <https://forumautomation.com/t/difference-between-calibration-ranging-what-is-up-tests-and-down-tests-in-calibration/6605>\
**Category:** Calibration\
**Created:** [June 24, 2019, 6:53pm UTC](https://forumautomation.com/t/difference-between-calibration-ranging-what-is-up-tests-and-down-tests-in-calibration/6605 "2019-06-24T18:53:10Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![sivaranjith](https://forumautomation.com/letter_avatar_proxy/v4/letter/s/ba9def/32.png) [@sivaranjith](https://forumautomation.com/u/sivaranjith)\
**Post date:** [June 24, 2019, 6:53pm UTC](https://forumautomation.com/t/difference-between-calibration-ranging-what-is-up-tests-and-down-tests-in-calibration/6605/1 "2019-06-24T18:53:11Z")

</div>

[**Calibration**](https://forumautomation.com/c/field-instrumentation/calibration) and range are two tasks related to the determination of an accurate correspondence between the input signal of any instrument and its output signal.

 ![calibration1](https://cdn.forumautomation.com/original/2X/e/eb1a0893737d1acab95cd041b4081a667bd94940.jpeg)

Calibration ensures that the tool allows the real-world variable to be measured or controlled correctly. Simply defined, range sets the required connection between the input and output of an instrument.

Calibration VS Ranging:

Calibration

Calibrating an instrument means checking and adjusting its reaction (if needed) so that the output corresponds correctly to its input over a defined range. To do this, a real input stimulus of the exactly known amount must be exposed to the tool.

For pressure instrument this would mean subjecting the pressure instrument to known fluid conditions for a [**pressure gage**](https://forumautomation.com/t/types-of-pressure-gauge-based-on-the-working-principle/2709), indicator, or transmitter and comparing the reaction of the tool to those known pressure amounts. Without comparing the response of an instrument to known physical stimuli, one can not conduct a real calibration.

Ranging:

Ranging an instrument means setting the reduced and upper range values in order to respond to modifications in input with the required sensitivity.

For example, a pressure transmitter set to a range of 0 to 200 PSI (0 PSI = 4 mA output ; 200 PSI = 20 mA output) could be re-ranged to respond on a scale of 0 to 150 PSI (0 PSI = 4 mA ; 150 PSI = 20 mA).

Re-ranging could (generally) only be achieved by re-calibration in analog tools since the same modifications were used for both times. Calibration and range are typically distinct modifications in digital tools (i.e. a digital transmitter can be re-ranged without having to conduct a full recalibration), so understanding the distinction is essential.

Up-tests and Down-tests

Calibration tables showing various up and down calibration points for documenting hysteresis and deadband mistakes. Note the table below, displaying a transmitter with 0.313 percent peak hysteresis:

 ![cal%20tab](https://cdn.forumautomation.com/original/2X/7/77095830aa050c7c82e70012d83bc05e2a313657.png)

It is important not to over-shoot any of the test points during such a directional calibration test. If you over-shoot a test point when setting up one of the instrument’s input circumstances, merely “back up” the test stimulus and re-approachthe test point in the same direction as before. Unless the value of each test point is approached in the right direction,