# CT Nameplate Parameters

**URL:** <https://forumautomation.com/t/ct-nameplate-parameters/13876>\
**Category:** Electrical\
**Tags:** transformer\
**Created:** [February 10, 2026, 2:18pm UTC](https://forumautomation.com/t/ct-nameplate-parameters/13876 "2026-02-10T14:18:37Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Rabert](https://forumautomation.com/user_avatar/forumautomation.com/rabert/32/6784_2.png) [@Rabert](https://forumautomation.com/u/Rabert)\
**Post date:** [February 10, 2026, 2:18pm UTC](https://forumautomation.com/t/ct-nameplate-parameters/13876/1 "2026-02-10T14:18:38Z")

</div>

## CT NAMEPLATE PARAMETERS

## 1). Rated Primary Current (Ip)

Example:

• 400 A

• 800/400/200 A (multi-ratio)

## 2). Rated Secondary Current (Is)

• 5A (most common for LV/MV panels)

• 1A (long cable runs, reduces burden losses)

## 3). CT Ratio

Example:

• 400/5

• 800/1

If multi-ratio:

• 800-400-200/1

## 4). Burden (VA)

Example:

• 5 VA

• 10 VA

• 15 VA

• 30 VA

This means the CT can supply that many volt-amperes without exceeding accuracy limits.

## 5). Accuracy Class

Examples:

• Metering: 0.2, 0.5, 1.0

• Protection: 5P10, 5P20, 10P10

• Special: PX, PR

## 6). Frequency

• 50 Hz (India)

• 60 Hz (US)

## 7). Insulation Level

Example for 11 kV CT:

• 12/28/75 kV

Meaning

• 12 kV → rms working

• 28 kV → 1-min power-frequency withstand

• 75 kV → lightning impulse withstand

 ![image](https://cdn.forumautomation.com/original/2X/3/32082b7550d50ba275554019e9effbf172f6f785.jpeg)

## 8). Thermal Short-Time Current (Ith)

CT must survive short-circuit for 1 second.

Example:

• 25 kA, 1 sec

• 31.5 kA, 1 sec

## 9). Dynamic Current (Idyn)

Withstand peak current (electrodynamic forces).

Typically:

I\_dyn = 2.5 x I\_th

Example:

If Ith = 25 kA → Idyn ≈ 62.5 kA

## 10). Knee Point Voltage (Vk) (ONLY for PX class)

Example:

• Vk ≥ 120 V

• Vk ≥ 150 V

Important for differential relay operation.

## 11). Magnetizing Current (Im)

Typical:

• ≤ 30 mA at Vk/2

## 12). Secondary Winding Resistance (Rct)

Given in ohms.

Used for checking:

• Volt-drop

• CT saturation

• Relay burden calculation

## 13). Polarity Marking (P1, P2, S1, S2)

Important for CT orientation.

• P1 → Towards the source

• P2 → Towards the load

• S1 → Relay/meter positive

• S2 → Common/neutral

## 14). CT Type

• Wound type

• Bar type

• Ring type (core type)

## 15). Thermal Rating Factor (TRF)

Example:

• 1.2 times continuous current

Means CT can carry 20% overload continuously.

## 16). Standards (IS/IEC)

• IEC 61869-2

• IS 16227-2 1. Rated Primary Current (Ip)