# Comparison between of Thermocouple and RTD ( Advantages and Disadvantages)

**URL:** <https://forumautomation.com/t/comparison-between-of-thermocouple-and-rtd-advantages-and-disadvantages/4565>\
**Category:** Temperature Measurement\
**Created:** [September 6, 2018, 12:17pm UTC](https://forumautomation.com/t/comparison-between-of-thermocouple-and-rtd-advantages-and-disadvantages/4565 "2018-09-06T12:17:59Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![sivaranjith](https://forumautomation.com/letter_avatar_proxy/v4/letter/s/ba9def/32.png) [@sivaranjith](https://forumautomation.com/u/sivaranjith)\
**Post date:** [September 6, 2018, 12:17pm UTC](https://forumautomation.com/t/comparison-between-of-thermocouple-and-rtd-advantages-and-disadvantages/4565/1 "2018-09-06T12:17:59Z")

</div>

[Thermocouple](https://automationforum.co/thermocouple-basics-types-thermocouple/) and [RTDs](https://automationforum.co/resistance-temperature-detector-rtd/) are the two important temperature measuring devices used widely in industries. They are compared on their purpose.

> # Thermocouple:

## Advantages:

**Cost:** Comparing to RTD, Thermocouple is lesser expensive.

**Temperature Range:** Extends to about 1150°C or higher. However, the thermocouple’s cryogenic range is somewhat less than that of the RTD.

**Mounting cost:** Lower than RTD

**Ruggedness:** For process environmental condition, high temperature, vibration, thermocouple are regarded highly.

## Disadvantages:

**Stability:** Less than for the RTD. Estimated at 0.6◦C (1◦F) per year.

**Calibration:** Nonlinear over normal spans. Signal requires linearizing. Calibration can be changed by contamination.

**Accuracy:** Generally expected, after installation, ±4◦C (±7.2◦F), but there are exceptions. Thermocouple requires reference junction or special wires. The inaccuracy is due to two separate temperature measurements - the measuring junction and the cold or reference junction.

> # RTD:

## Advantages:

**Accuracy:** Accepted after installation ±0.5◦C. The platinum RTD, for example, is used to define the IPTS at the oxygen point (−182.97◦C) and the antimony point (+630.74◦C).

**Repeatability:** Within a few hundredths of a degree; can often be achieved with platinum RTDs. Less than 0.1% drift in 5 years.

**Relatively narrow spans:** Some versions may have spans as narrow as 5.6◦C (10◦F).

**Substantial output voltage (1 to 6 volts):** This is an advantage in that the output can be controlled by adjusting the current and the bridge design in the RTD signal conversion module. Because of a higher output voltage to the RTD and controlling of temperature signals is simpler. This permits more accurate measurements without requiring complex calculations for large spans

**Compensation:** Not required.

**Size:** Generally smaller than thermocouples

## Disadvantages:

**Cost:** Higher than the thermocouple. RTDs do not require compensation, special lead-wires, and special signal conditioning for long runs.

**Less rugged:** For adverse process environments, including high temperature and vibration.

**Lower temperature range:** Limited to about 870◦C (1600◦F).

**Self-heating errors:** This may be a problem unless corrected in the transistor’s electronics.