**is it possible to use a pressure switch as a level switch**

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [November 5, 2020, 4:46am UTC](https://forumautomation.com/t/can-we-use-pressure-switch-as-level-switch/8782/2 "2020-11-05T04:46:59Z")

</div>

Yes, but the range needs to be checked and the calibration required as per the level switching point.

Yes, we can use it by knowing the static head of the liquid column.