# Can control valve work without positioner?

**URL:** <https://forumautomation.com/t/can-control-valve-work-without-positioner/10038>\
**Category:** Field Instrumentation\
**Created:** [December 6, 2021, 3:46am UTC](https://forumautomation.com/t/can-control-valve-work-without-positioner/10038 "2021-12-06T03:46:14Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [December 6, 2021, 3:46am UTC](https://forumautomation.com/t/can-control-valve-work-without-positioner/10038/1 "2021-12-06T03:46:14Z")

</div>

Is it possible to operate a control valve without a positioner

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [December 6, 2021, 3:55am UTC](https://forumautomation.com/t/can-control-valve-work-without-positioner/10038/2 "2021-12-06T03:55:47Z")

</div>

Yes, many control valves have I/P’s connected directly to single-acting actuators. A controller with PID will look at the process variable (PV) to increase or decrease the signal to I/P so that PV matches the setpoint.

It can still work with an I to P.

A Positioner is just an I to P (transducer) with position feedback, for better control.

An I to P will take in the 4-20mA signal and put out an equivalent air pressure, whether it is 3-15PSI or 6-30PSI, whichever you set it up for.