# Calibration of a static head level transmitter for an interface measurement

**URL:** <https://forumautomation.com/t/calibration-of-a-static-head-level-transmitter-for-an-interface-measurement/66>\
**Category:** Calibration\
**Created:** [October 2, 2014, 5:52pm UTC](https://forumautomation.com/t/calibration-of-a-static-head-level-transmitter-for-an-interface-measurement/66 "2014-10-02T17:52:31Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumen](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/65b543/32.png) [@instrumen](https://forumautomation.com/u/instrumen)\
**Post date:** [October 2, 2014, 5:52pm UTC](https://forumautomation.com/t/calibration-of-a-static-head-level-transmitter-for-an-interface-measurement/66/1 "2014-10-02T17:52:31Z")

</div>

Static head level transmitter is not commonly used for measuring the interface level. But the following procedure may be used for calibrating it to measure the interface level in a tank. Fill the vessel 100% with the lower density liquid and adjusts its zero for 4.00 mA output. Drain the liquid and fill with the vessel 100% with the higher density liquid and adjust its span for 20.00mA output. 100% transmitter level is to be continuously maintained. The transmitter on line measures the percentage of higher density liquid in the lower density liquid in a know height.