# Calculate the output in mA of Electronics D.P Tx. When applied a D.P of 125 inches of water gauge, knowing that the range is 0 to 300 inches of WG?

**URL:** <https://forumautomation.com/t/calculate-the-output-in-ma-of-electronics-d-p-tx-when-applied-a-d-p-of-125-inches-of-water-gauge-knowing-that-the-range-is-0-to-300-inches-of-wg/12060>\
**Category:** Calibration\
**Tags:** interviewquestions\
**Created:** [May 13, 2024, 5:25pm UTC](https://forumautomation.com/t/calculate-the-output-in-ma-of-electronics-d-p-tx-when-applied-a-d-p-of-125-inches-of-water-gauge-knowing-that-the-range-is-0-to-300-inches-of-wg/12060 "2024-05-13T17:25:28Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![Sundar\_Iyalunaidu](https://forumautomation.com/user_avatar/forumautomation.com/sundar_iyalunaidu/32/7404_2.png) [@Sundar\_Iyalunaidu](https://forumautomation.com/u/Sundar_Iyalunaidu)\
**Post date:** [May 13, 2024, 5:25pm UTC](https://forumautomation.com/t/calculate-the-output-in-ma-of-electronics-d-p-tx-when-applied-a-d-p-of-125-inches-of-water-gauge-knowing-that-the-range-is-0-to-300-inches-of-wg/12060/1 "2024-05-13T17:25:28Z")

</div>

Calculate the output in mA of Electronics D.P Tx. When applied a D.P of 125 inches of water gauge, knowing that the range is 0 to 300 inches of WG?

 ![image](https://cdn.forumautomation.com/original/2X/1/1722cff4c1ce3d9c6dc1a332b9f9eee418118f84.jpeg)

---

<div class="post-metadata">

**Author:** ![Instrument\_Engineer](https://forumautomation.com/user_avatar/forumautomation.com/instrument_engineer/32/6734_2.png) [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Post date:** [May 14, 2024, 3:06pm UTC](https://forumautomation.com/t/calculate-the-output-in-ma-of-electronics-d-p-tx-when-applied-a-d-p-of-125-inches-of-water-gauge-knowing-that-the-range-is-0-to-300-inches-of-wg/12060/2 "2024-05-14T15:06:49Z")

</div>

To calculate the output current in mA for an electronic differential pressure transmitter (D.P Tx) with a range of 0 to 300 inches of water gauge (WG), you can use the following formula:

 ![image](https://cdn.forumautomation.com/original/2X/1/1723cb3cee5bdf48fe4f2beda0ad0f8a2323996b.png)

Where:

- ( DP ) is the differential pressure applied.
- ( LRV ) is the lower range value, which is 0 inches of WG in this case.
- ( URV ) is the upper range value, which is 300 inches of WG.
- ( Span ) is the difference between the maximum and minimum output current, which is typically 16 mA (20 mA - 4 mA for a 4-20 mA transmitter).

Given that the applied ( DP ) is 125 inches of WG, the calculation would be:

![image](https://cdn.forumautomation.com/original/2X/8/82b60edf008d6c73ce04435d79da10458035e51d.png)

So, the output current would be **10.667 mA** when a differential pressure of 125 inches of WG is applied to the transmitter.

---

<div class="post-metadata">

**Author:** ![Instrument\_Engineer](https://forumautomation.com/user_avatar/forumautomation.com/instrument_engineer/32/6734_2.png) [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Post date:** [May 14, 2024, 3:10pm UTC](https://forumautomation.com/t/calculate-the-output-in-ma-of-electronics-d-p-tx-when-applied-a-d-p-of-125-inches-of-water-gauge-knowing-that-the-range-is-0-to-300-inches-of-wg/12060/3 "2024-05-14T15:10:52Z")

</div>

Refer the below online calculator link

> **[PV into 4-20mA scaling calculator](https://automationforum.co/pv-into-4-20ma-scaling-calculator/)**
>
> This calculator used find the 4 to 20 mA output from the process value from the field instruments with accuracy.