# Bus Protection Functions & Systems

## 1). Primary Bus Protection (High-Speed - Main)

• 87B – Bus Differential: Compares all feeder currents and trips instantly for internal bus faults.

• 87BB – Dedicated Busbar Diff: Separate relay only for bus zone security.

• 87Z – Zone/Sectional Diff: Protects individual bus sections in double bus systems.

• 87N – Neutral Differential: Used in LV/MV grounded buses.

• 87ST – Stub Diff: Protects breaker-and-half / ring bus dead zones.

• 64REF – Restricted EF: Highly sensitive earth fault inside bus zone.

• 64 – Sensitive GF: Detects very low ground currents.

These are the MAIN FAST protections in all **[substations.](https://forumelectrical.com/what-causes-dc-system-failures-in-substations/)**

## 2). Backup Overcurrent & Earth Fault

• 50 – Instant Phase OC: No delay, close-in fault clearing.

• 51 – Time OC: Graded with feeders for coordination.

• 50N / 51N – Instant & Time EF: Earth fault backup.

• 51G – Neutral CT EF: For **[transformer](https://forumelectrical.com/transformer-voltage-regulation-calculator/)**/bus grounding path.

• 50HS – High-set backup: Last defense for severe faults.

• 46 – Negative Sequence: Unbalance & phase loss.

• 67 / 67N – Directional OC & EF: Needed for multi-source buses.

Used as backup in every scheme.

## 3). Breaker Failure & Tripping

• 50BF – Breaker Failure: Trips upstream if CB doesn’t open.

• 86 – Lockout: Latches trip for safety.

• 94 – Trip Multiplier: Fan-out trip to many breakers.

• 52 – CB Status: Open/close supervision.

Important for reliability of any protection system.

## 4). Supervision & Monitoring

• 60 – CT/VT Fuse Fail: Avoids false trips.

• 74 – Trip Circuit Supervision: Checks coil wiring.

• 30 – Annunciator: Alarm display.

• 95 – Trip Blocking Logic: Interlock safety.

Operational health monitoring.

## 5). Voltage & Stability

• 27 – Undervoltage

• 59 – Overvoltage

• 81O/U – Frequency

• 78 – Out-of-Step

• 32 – Reverse Power

Grid stability protections.

 ![image](https://cdn.forumautomation.com/original/2X/4/4011a2d3032ac984cf57e693e84af3f8249ed870.jpeg)

## 6). Communication & Logic

• 85 – GOOSE/Pilot communication

• 43 – Selector switch

• 68 – Power swing block

• 69 – Permissive interlock

**[IEC-61850](https://forumelectrical.com/top-12-iec-standards-in-electrical-engineering/)** based modern schemes.

## 7). Bus Transfer & Restoration

• 25 – Sync check

• 79 – Auto reclose

• 21 – Distance backup (EHV)

## 8). Equipment / Thermal

• 49 – Thermal overload

• 26 – Temperature supervision

Protects bus ducts & metal clad panels.