is this scaling of analog input PIW290?

 ![image](https://cdn.forumautomation.com/original/2X/3/351ad579c8d54bc9ddae25c0f41814cd25d3199c.jpeg)

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [May 26, 2021, 4:16am UTC](https://forumautomation.com/t/analog-input-in-plc-programming/9433/2 "2021-05-26T04:16:02Z")

</div>

It is the Analog input from the field.

HI\_LIM is the upper value of the range of the instrument

LO\_LIM is the lower value of the range of the instrument

BIPOLAR = FALSE means the IN cannot go negative you have only positive values.

RET\_VAL is used to detect broken wire in 4-20 mA or conversion problems. 16#8000 is a broken wire.

OUT ([#outval](https://www.facebook.com/hashtag/outval? __eep__ =6& __cft__ %5B0%5D=AZVIYkixaXgM7GidqLsGo-qGYwYDLowVBYMJCw400gpzP_x0o3pl-rYbvfbs7KI9Bgcw8Vkef_xn8hR20mYVtqcN1b3eVENbz0xU6TxuaEu-3Q2poQzJLwhlyQemVmRcZYWHNLOXcYnWvOCt1-f1bsW7ArrwKsR4Fb8zE5z_fbzSnvoxjmY98WILfz1vpD3xyUmvkM1rTl3QueZpPI7d3PZR& __tn__ =R%5D-R)) is the out of the FC must be a REAL

MD84 must be REAL in order to have a consistent number.