# A pressure-relief valve has a pressure setting of 140 bar. Compute the kW loss across this valve if it returns all the flow back to the tank from a 0.0016 3 m / s pump

**URL:** <https://forumautomation.com/t/a-pressure-relief-valve-has-a-pressure-setting-of-140-bar-compute-the-kw-loss-across-this-valve-if-it-returns-all-the-flow-back-to-the-tank-from-a-0-0016-3-m-s-pump/12146>\
**Category:** Valves\
**Tags:** interviewquestions\
**Created:** [June 7, 2024, 12:07pm UTC](https://forumautomation.com/t/a-pressure-relief-valve-has-a-pressure-setting-of-140-bar-compute-the-kw-loss-across-this-valve-if-it-returns-all-the-flow-back-to-the-tank-from-a-0-0016-3-m-s-pump/12146 "2024-06-07T12:07:31Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![Sundar\_Iyalunaidu](https://forumautomation.com/user_avatar/forumautomation.com/sundar_iyalunaidu/32/7404_2.png) [@Sundar\_Iyalunaidu](https://forumautomation.com/u/Sundar_Iyalunaidu)\
**Post date:** [June 7, 2024, 12:07pm UTC](https://forumautomation.com/t/a-pressure-relief-valve-has-a-pressure-setting-of-140-bar-compute-the-kw-loss-across-this-valve-if-it-returns-all-the-flow-back-to-the-tank-from-a-0-0016-3-m-s-pump/12146/1 "2024-06-07T12:07:31Z")

</div>

A pressure-relief valve has a pressure setting of 140 bar. Compute the kW loss across this valve if it returns all the flow back to the tank from a 0.0016 3 m / s pump.

 ![image](https://cdn.forumautomation.com/original/2X/9/9f7e0d0f88a01b58951133645c1232803d08f95e.jpeg)

---

<div class="post-metadata">

**Author:** ![Instrument\_Engineer](https://forumautomation.com/user_avatar/forumautomation.com/instrument_engineer/32/6734_2.png) [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Post date:** [June 14, 2024, 4:35pm UTC](https://forumautomation.com/t/a-pressure-relief-valve-has-a-pressure-setting-of-140-bar-compute-the-kw-loss-across-this-valve-if-it-returns-all-the-flow-back-to-the-tank-from-a-0-0016-3-m-s-pump/12146/2 "2024-06-14T16:35:26Z")

</div>

To compute the power loss across the pressure-relief valve, we can use the formula for hydraulic power loss, which is given by:

P=ΔP×Q

Where:

- P is the power loss (in watts, W).
- ΔP\Delta PΔP is the pressure difference across the valve (in pascals, Pa).
- QQQ is the flow rate (in cubic meters per second, m³/s).

Given:

- The pressure setting of the valve ΔP is 140 bar.
- The flow rate Q from the pump is 0.0016 m³/s.

First, we need to convert the pressure setting from bar to pascals:

 ![image](https://cdn.forumautomation.com/original/2X/2/20803b232bce33f848f9e962e9ba19e360e5205f.png)

Now we can plug the values into the formula: ![image](https://cdn.forumautomation.com/original/2X/f/fffafc3d3e247780168248ae5eafe1a5fc960bd0.png)

Calculating this gives:

P=22,400 W

Since 1 kilowatt (kW) is equal to 1,000 watts (W), we convert the power loss to kilowatts:

![image](https://cdn.forumautomation.com/original/2X/3/337fdcecdac400cd1b242ba6a932e8f14e0f3569.png)

Therefore, the power loss across the pressure-relief valve is 22.4 kW.