Why 4mA in 4-20mA standard is used and why not 3mA or 5mA?

---

<div class="post-metadata">

**Author:** ![carl\_e](https://forumautomation.com/letter_avatar_proxy/v4/letter/c/94ad74/32.png) [@carl\_e](https://forumautomation.com/u/carl_e)\
**Post date:** [June 23, 2020, 12:59pm UTC](https://forumautomation.com/t/4-20ma-current-significance/8030/2 "2020-06-23T12:59:14Z")

</div>

The answer to your question as to why the lower range value is 4.0mA is because that’s the standard, defined by an international standard ANSI/ISA-50-1975 (2002), originally adopted, as the date in the title shows, in 1975.

The creation of the standard lagged the development and adoption of the 4-20 range by at least a decade, meaning the most of the majors in the process industry had effectively settled on the 4-20mA range by the time the standard was created. The main hold-out and competitor to 4-20mA was 10-50mA used by Foxboro, which did have an advantage where more loop power was needed, say to drive split-ranged valve positioners in series.

The reason for a ‘live zero’, a minimum value above zero, is that 2-wire field instruments use 3.5mA to power the device’s electronics that make the measurement and to control the regulated output. The fact that a live zero provides a diagnostic of an open loop/wire break if the loop current drops to zero is a nice/convenient feature, but was not the main reason for a live zero, the ability to power 2-wire field instruments was the main reason.

The 1:5 ratio of 4:20 followed the pneumatic ratio of the then standard 3-15 PSI. The same reason for a minimum 3 PSI applies - the operation of pneumatic controls required some on-going, continuous consumption of air (air bleed through the flapper valve) so having zero pressure would eliminate the ability to use air to make the measurement. A live zero was necessary to make the measurement and control the regulated output.

A second serious consideration in the adoption of 4-20mA was the magnitude of circuit energy that could be handled through Intrinsic Safety concepts and engineering for use in hazardous areas.

The industry effectively adopted 4-20mA before the standard because 4-20mA could power field instruments over 2 wires, fit the accepted 1:5 ratio, ‘offered a live zero’, and could be intrinsically safe (with associated apparatus).