This is a thumb rule-based approach; use it as a starting point before going into extensive calculations and guidelines for appropriate electrical design.

**1. Load (kW)**

Load (kW) = √3 × V × I × PF / 1000 To calculate 3-phase power 3Φ, 400V, 50A, PF=0.8 → Load = 27.71 kW

**2** **. Current (I)**

Current (I) = Load (kW) × 1000 / (√3 × V × PF) To estimate current from known power 30 kW, 400V, PF=0.9 → I ≈ 48.1 A

**3**  **. Horsepower**

1 HP = 0.746 kW Convert motor horsepower to kilowatt 5 HP motor → 3.73 kW

**4**  **. KVA**

1 kVA = 0.8 kW (for PF=0.8) Estimate real power from apparent power 50 kVA DG → 40 kW (approx.)

**5**  **. Demand Factor**

Demand Factor ≈ 0.6 to 0.8 Total connected load × DF = estimated actual demand 100 kW connected → 70 kW (DF=0.7)

**6**  **. Diversity Factor**

Diversity Factor = Total Connected Load / Maximum Demand Used in panel and feeder sizing 200 kW connected / 120 kW demand = 1.67

**7** **. Voltage Drop (V)**

Voltage Drop (V) = √3 × I × L × R / 1000 Voltage drop in 3Φ system; R = resistance (Ω/km) I=100A, L=50m, R=0.3 Ω/km → Vdrop = 2.6V

**8**  **. Max Allowable VDrop**

3–5% As per standard for final circuits 400V system: Max Vdrop = 20V

**9**  **. Current Carrying Capacity**

1 sq.mm copper cable ≈ 6-7 A Current carrying capacity (rule of thumb) 10 sq.mm cable → ~65 A

**10. Cable Derating Factor**

0.7–0.9 Adjust cable ampacity in hot areas or bunching 70 A × 0.8 = 56 A actual.