# Level Measurement

**URL:** https://forumautomation.com/c/field-instrumentation/level-measurement/38.md?page=1

[Latest](https://forumautomation.com/latest.md) · [Categories](https://forumautomation.com/categories.md) · [Tags](https://forumautomation.com/tags.md)

**Page:** 2

---

## [Level measurement sensor technologies and how to select suitable level measurement instrument for your application?](https://forumautomation.com/t/level-measurement-sensor-technologies-and-how-to-select-suitable-level-measurement-instrument-for-your-application/1196)

<div class="topic-metadata">

**Author:** [@denizen](https://forumautomation.com/u/denizen)\
**Replies:** 0\
**Last updated:** [July 25, 2016, 12:34am UTC](https://forumautomation.com/t/level-measurement-sensor-technologies-and-how-to-select-suitable-level-measurement-instrument-for-your-application/1196 "2016-07-25T00:34:50Z")

</div>

Different types of level measurement technologies are available. Based on the application right level measurement instrument must be selected for accurate level measurement. Types of level measurement instruments availa…

---

## [Drum gauge level measurement for chemical](https://forumautomation.com/t/drum-gauge-level-measurement-for-chemical/4813)

<div class="topic-metadata">

**Author:** [@sivaranjith](https://forumautomation.com/u/sivaranjith)\
**Replies:** 0\
**Last updated:** [October 1, 2018, 5:36pm UTC](https://forumautomation.com/t/drum-gauge-level-measurement-for-chemical/4813 "2018-10-01T17:36:34Z")

</div>

Drum gauge is one of the important parts of chemical injection equipment and is used to measure chemical levels. Equipped with a spring-loaded test valve which is useful for a testing injection rate of the chemical pump;…

---

## [What is the Blocking Distance (blind range, dead zone) for Radar Level Measurements?](https://forumautomation.com/t/what-is-the-blocking-distance-blind-range-dead-zone-for-radar-level-measurements/11883)

<div class="topic-metadata">

**Author:** [@Rabert](https://forumautomation.com/u/Rabert)\
**Replies:** 0\
**Last updated:** [March 20, 2024, 7:48am UTC](https://forumautomation.com/t/what-is-the-blocking-distance-blind-range-dead-zone-for-radar-level-measurements/11883 "2024-03-20T07:48:31Z")

</div>

What is the Blocking Distance (blind range, dead zone) for Radar Level Measurements? The blocking distance occurs when the level is too close to the radar instrument; reflections are no longer received when the radar emi…

---

## [How to Avoid Temperature Effects in Differential Pressure Level Measurements?](https://forumautomation.com/t/how-to-avoid-temperature-effects-in-differential-pressure-level-measurements/11356)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 0\
**Last updated:** [August 2, 2023, 1:57pm UTC](https://forumautomation.com/t/how-to-avoid-temperature-effects-in-differential-pressure-level-measurements/11356 "2023-08-02T13:57:56Z")

</div>

In this type of application, the differential pressure transmitter measures the pressure of the media in the tank, the pressure at the top of the tank, and the head pressure made by the fill fluid in the capillary. A…

---

## [What are the applications of Guided wave radar level transmitter?](https://forumautomation.com/t/what-are-the-applications-of-guided-wave-radar-level-transmitter/698)

<div class="topic-metadata">

**Author:** [@denizen](https://forumautomation.com/u/denizen)\
**Replies:** 0\
**Last updated:** [December 30, 2015, 2:09am UTC](https://forumautomation.com/t/what-are-the-applications-of-guided-wave-radar-level-transmitter/698 "2015-12-30T02:09:22Z")

</div>

Guided wave radar is suitable for a variety level measurement applications 1.Unstable process conditions - Changes in viscosity,density or acidity do not affect affect accuracy 2.Agitated surfaces - Boiling surfaces,d…

---

## [Level measurement errors](https://forumautomation.com/t/level-measurement-errors/2554)

<div class="topic-metadata">

**Author:** [@sivaranjith](https://forumautomation.com/u/sivaranjith)\
**Replies:** 0\
**Last updated:** [November 2, 2017, 8:07pm UTC](https://forumautomation.com/t/level-measurement-errors/2554 "2017-11-02T20:07:16Z")

</div>

Differential pressure transmitters are used to pressure exerted by a level of water in a vessel. This places great importance on the physical and environmental problems that can affect the accuracy of this indirect measu…

---

## [What are the types of Level Gauges and its applications?](https://forumautomation.com/t/what-are-the-types-of-level-gauges-and-its-applications/9774)

<div class="topic-metadata">

**Author:** [@Ajmal\_ismail](https://forumautomation.com/u/Ajmal_ismail)\
**Replies:** 0\
**Last updated:** [August 20, 2021, 11:59am UTC](https://forumautomation.com/t/what-are-the-types-of-level-gauges-and-its-applications/9774 "2021-08-20T11:59:47Z")

</div>

What is Level Gauges? Level Gauges is a type of meter used to determine the amount of liquid in a fixed storage or process tank. The head, float, tape, lower anchored bracket, guide wires, elbows, anchors, coupling, pip…

---

## [Selection of level measurement equipment?](https://forumautomation.com/t/selection-of-level-measurement-equipment/440)

<div class="topic-metadata">

**Author:** [@denizen](https://forumautomation.com/u/denizen)\
**Replies:** 0\
**Last updated:** [June 7, 2015, 7:07am UTC](https://forumautomation.com/t/selection-of-level-measurement-equipment/440 "2015-06-07T07:07:17Z")

</div>

Level measurement equipment selection Major categories of level measurement equipment selection 1)Will the installation be internal or external ? 2)Will the measurement be direct or indirect measurement ? Direct measur…

---

## [What is the reason for using dry elements instead of wet elements when measuring fluid level with capacitance sensors?](https://forumautomation.com/t/what-is-the-reason-for-using-dry-elements-instead-of-wet-elements-when-measuring-fluid-level-with-capacitance-sensors/12460)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 2\
**Last updated:** [September 2, 2024, 5:11pm UTC](https://forumautomation.com/t/what-is-the-reason-for-using-dry-elements-instead-of-wet-elements-when-measuring-fluid-level-with-capacitance-sensors/12460 "2024-09-02T17:11:20Z")

</div>

What is the reason for using dry elements instead of wet elements when measuring fluid level with capacitance sensors?

---

## [Interview Questions - What are the common continuous liquid level measurement methods?](https://forumautomation.com/t/interview-questions-what-are-the-common-continuous-liquid-level-measurement-methods/427)

<div class="topic-metadata">

**Author:** [@denizen](https://forumautomation.com/u/denizen)\
**Replies:** 0\
**Last updated:** [May 19, 2015, 4:25am UTC](https://forumautomation.com/t/interview-questions-what-are-the-common-continuous-liquid-level-measurement-methods/427 "2015-05-19T04:25:12Z")

</div>

The common methods employed for automatic continuous liquid level measurements are 1.Float and Cable 2.Displacement (buoyancy) 3.Head(Pressure) 4.Capacitance 5.Conductance 6.Radiation 7.Weight 8.Ultrasonic 9.Thermal

---

## [Exploring the Limitations of Ultrasonic Level Measurement in Industrial Applications](https://forumautomation.com/t/exploring-the-limitations-of-ultrasonic-level-measurement-in-industrial-applications/11480)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 0\
**Last updated:** [September 20, 2023, 1:41am UTC](https://forumautomation.com/t/exploring-the-limitations-of-ultrasonic-level-measurement-in-industrial-applications/11480 "2023-09-20T01:41:55Z")

</div>

In numerous industrial applications, ultrasonic level measurement is a commonly utilized method for determining the level of liquid or solid materials. It has a lot of benefits, like non-contact measurement and simpl…

---

## [What is drum level control in HRSG?](https://forumautomation.com/t/what-is-drum-level-control-in-hrsg/13319)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [June 21, 2025, 5:24am UTC](https://forumautomation.com/t/what-is-drum-level-control-in-hrsg/13319 "2025-06-21T05:24:13Z")

</div>

What is drum level control in HRSG?

---

## [Interface in level measurement](https://forumautomation.com/t/interface-in-level-measurement/63)

<div class="topic-metadata">

**Author:** [@instrumen](https://forumautomation.com/u/instrumen)\
**Replies:** 0\
**Last updated:** [October 2, 2014, 5:49pm UTC](https://forumautomation.com/t/interface-in-level-measurement/63 "2014-10-02T17:49:21Z")

</div>

An interface is the separation point between the two de-missible liquids levels In a vessel. This condition arises when the liquid does not mix due to its chemical composition and difference in their density.

---

## [Selection of a level switch for a particular process](https://forumautomation.com/t/selection-of-a-level-switch-for-a-particular-process/61)

<div class="topic-metadata">

**Author:** [@instrumen](https://forumautomation.com/u/instrumen)\
**Replies:** 0\
**Last updated:** [October 2, 2014, 5:46pm UTC](https://forumautomation.com/t/selection-of-a-level-switch-for-a-particular-process/61 "2014-10-02T17:46:06Z")

</div>

While selecting a level switch, the following points are to be considered: The characteristic of process (corrosive or non – corrosive) The process pressure The liquid density The flange ratings Proof pressure of the s…

---

## [Issue with interface leveltrol - displacer type level transmitter](https://forumautomation.com/t/issue-with-interface-leveltrol-displacer-type-level-transmitter/12223)

<div class="topic-metadata">

**Author:** [@automation\_engineer6](https://forumautomation.com/u/automation_engineer6)\
**Replies:** 1\
**Last updated:** [July 1, 2024, 1:06pm UTC](https://forumautomation.com/t/issue-with-interface-leveltrol-displacer-type-level-transmitter/12223 "2024-07-01T13:06:41Z")

</div>

I’m experiencing issues with the interface leveltrol in one of our crude oil storage tanks. The leveltrol is showing erratic readings and sometimes fails to detect the correct oil-water interface. I’ve already checked fo…

---

## [Do wet leg of differential pressure transmitter in closed level tank has different SG (Specific Gravity)? Justify](https://forumautomation.com/t/do-wet-leg-of-differential-pressure-transmitter-in-closed-level-tank-has-different-sg-specific-gravity-justify/11124)

<div class="topic-metadata">

**Author:** [@Sudha\_m](https://forumautomation.com/u/Sudha_m)\
**Replies:** 0\
**Last updated:** [May 4, 2023, 4:38pm UTC](https://forumautomation.com/t/do-wet-leg-of-differential-pressure-transmitter-in-closed-level-tank-has-different-sg-specific-gravity-justify/11124 "2023-05-04T16:38:58Z")

</div>

In a closed level tank, the process fluid’s specific gravity (Sg) should be the same as the wet leg of the differential pressure (DP) transmitter. This is due to the fact that the hydrostatic pressure produced by the f…

---

## [What is zero elevation on a DP level transmitter?](https://forumautomation.com/t/what-is-zero-elevation-on-a-dp-level-transmitter/13772)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [December 13, 2025, 4:14am UTC](https://forumautomation.com/t/what-is-zero-elevation-on-a-dp-level-transmitter/13772 "2025-12-13T04:14:13Z")

</div>

What is zero elevation on a DP level transmitter?

---

## [Overfilled Protection For Storage Tanks](https://forumautomation.com/t/overfilled-protection-for-storage-tanks/7090)

<div class="topic-metadata">

**Author:** [@Noblestyle](https://forumautomation.com/u/Noblestyle)\
**Replies:** 0\
**Last updated:** [September 5, 2019, 12:17pm UTC](https://forumautomation.com/t/overfilled-protection-for-storage-tanks/7090 "2019-09-05T12:17:36Z")

</div>

Hello Team, Please I need advise on how to prevent spillage of storage tank content We have been having issues with product wastage and I am not looking at incorporating an overfilled protection on the storage tanks P…

---

## [How wet leg of dp transmitter in closed level tank maintained and not contaminated?](https://forumautomation.com/t/how-wet-leg-of-dp-transmitter-in-closed-level-tank-maintained-and-not-contaminated/11109)

<div class="topic-metadata">

**Author:** [@Sudha\_m](https://forumautomation.com/u/Sudha_m)\
**Replies:** 0\
**Last updated:** [May 3, 2023, 1:36pm UTC](https://forumautomation.com/t/how-wet-leg-of-dp-transmitter-in-closed-level-tank-maintained-and-not-contaminated/11109 "2023-05-03T13:36:08Z")

</div>

It is crucial to adhere to a few basic procedures in order to keep the wet leg of a differential pressure (DP) transmitter in a closed level tank and avoid contamination. Choose the Correct Fluid: The liquid used in th…

---

## [What is wet leg calibration?](https://forumautomation.com/t/what-is-wet-leg-calibration/13773)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [December 20, 2025, 1:10pm UTC](https://forumautomation.com/t/what-is-wet-leg-calibration/13773 "2025-12-20T13:10:15Z")

</div>

What is wet leg calibration?

---

## [What is the main advantage of hydrostatic level sensor type?](https://forumautomation.com/t/what-is-the-main-advantage-of-hydrostatic-level-sensor-type/13576)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [October 4, 2025, 4:39pm UTC](https://forumautomation.com/t/what-is-the-main-advantage-of-hydrostatic-level-sensor-type/13576 "2025-10-04T16:39:45Z")

</div>

What is the main advantage of hydrostatic level sensor type ?

---

## [Why Is My Fisher 249 Displacer Leveltrol Not Accepting Span Calibration When Using Water?](https://forumautomation.com/t/why-is-my-fisher-249-displacer-leveltrol-not-accepting-span-calibration-when-using-water/13715)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [November 15, 2025, 10:49am UTC](https://forumautomation.com/t/why-is-my-fisher-249-displacer-leveltrol-not-accepting-span-calibration-when-using-water/13715 "2025-11-15T10:49:34Z")

</div>

We are facing a calibration problem with a Fisher 249 displacer-type leveltrol installed side-mounted in a cage with a DVC controller. The application is crude oil (SG ≈ 0.8), used for both oil level and interface level …

---

## [What is the hydraulic method of level measurement?](https://forumautomation.com/t/what-is-the-hydraulic-method-of-level-measurement/13575)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [October 11, 2025, 10:07am UTC](https://forumautomation.com/t/what-is-the-hydraulic-method-of-level-measurement/13575 "2025-10-11T10:07:47Z")

</div>

What is the hydraulic method of level measurement?

---

## [Ultrasonic Liquid Level Transmitter: Non-Contact Level Measurement](https://forumautomation.com/t/ultrasonic-liquid-level-transmitter-non-contact-level-measurement/13733)

<div class="topic-metadata">

**Author:** [@ARTang](https://forumautomation.com/u/ARTang)\
**Replies:** 0\
**Last updated:** [November 27, 2025, 6:58am UTC](https://forumautomation.com/t/ultrasonic-liquid-level-transmitter-non-contact-level-measurement/13733 "2025-11-27T06:58:16Z")

</div>

An ultrasonic liquid level transmitter—also known as an ultrasonic level meter—is a non-contact, highly reliable, cost-effective, and easy-to-install liquid level measurement device. It can meet most level-measurement re…

---

## [How to Choose the Liquid Level Transmitter?](https://forumautomation.com/t/how-to-choose-the-liquid-level-transmitter/13669)

<div class="topic-metadata">

**Author:** [@ARTang](https://forumautomation.com/u/ARTang)\
**Replies:** 0\
**Last updated:** [October 31, 2025, 6:04am UTC](https://forumautomation.com/t/how-to-choose-the-liquid-level-transmitter/13669 "2025-10-31T06:04:29Z")

</div>

liquid level transmitter (hydrostatic liquid level meter / liquid level transmitter / liquid level sensor / water level sensor) is a kind of pressure sensor for measuring liquid level. Based on the principle that the sta…

---

## [Troubleshooting Ultrasonic Level Gauges in Measurement](https://forumautomation.com/t/troubleshooting-ultrasonic-level-gauges-in-measurement/13666)

<div class="topic-metadata">

**Author:** [@ARTang](https://forumautomation.com/u/ARTang)\
**Replies:** 0\
**Last updated:** [October 31, 2025, 6:01am UTC](https://forumautomation.com/t/troubleshooting-ultrasonic-level-gauges-in-measurement/13666 "2025-10-31T06:01:40Z")

</div>

Ultrasonic level gauges, as non-contact level measurement instruments, are known for their high measurement accuracy, simple installation, and minimal maintenance requirements. They are commonly used to measure the liqui…

---

## [Radar Level Transmitter Gives False Level Even Though the Actual Tank Level Is Stable](https://forumautomation.com/t/radar-level-transmitter-gives-false-level-even-though-the-actual-tank-level-is-stable/14353)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [September 5, 2026, 3:51am UTC](https://forumautomation.com/t/radar-level-transmitter-gives-false-level-even-though-the-actual-tank-level-is-stable/14353 "2026-09-05T03:51:11Z")

</div>

Radar Level Transmitter Gives False Level Even Though the Actual Tank Level Is Stable A radar level transmitter installed on a process vessel shows a level of 78 percent while the actual process level, confirmed through …

---

## [Capacitance Level Transmitter Shows Unstable Level Despite a Constant Process Level](https://forumautomation.com/t/capacitance-level-transmitter-shows-unstable-level-despite-a-constant-process-level/14333)

<div class="topic-metadata">

**Author:** [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Replies:** 1\
**Last updated:** [August 21, 2026, 1:40pm UTC](https://forumautomation.com/t/capacitance-level-transmitter-shows-unstable-level-despite-a-constant-process-level/14333 "2026-08-21T13:40:21Z")

</div>

Capacitance Level Transmitter Shows Unstable Level Despite a Constant Process Level A capacitance level transmitter is mounted on the process vessel to continually measure the liquid level. In normal operation the rea…

[Previous page](https://forumautomation.com/c/field-instrumentation/level-measurement/38.md?per_page=50)